John Peckham:
If fitted with fuses and the cover is missing then C2 and needs replacing.
John, why do you consider the cover to be so important please? If there is an interlock which allows the cover to be removed only when the main switch is off, I can see the point. However, I envisage just a rather flimsy cover secured by a wee knurled screw. If that can be removed whilst the fuses are still live, and IP2X is maintained, why not C3?
I might add that C3 hides a multitude of sins. I never felt inadequately protected when we had these fuse boxes when I was a small boy; but then again, I didn't feel inadequately protected before we has seatbelts.
AJJewsbury:I believe that this situation is in a residential mobile home park.
or perhaps in a brick shed housing the supply to them...?
- Andy.
"I need verification that it is ok to keep old style Wylex rewireable fuse boards to pass the EICR. Initially the electrician said this was ok providing they have a cover for the fuses. However he has now changed his mind and saying they need to be replaced with a new consumer unit. Some of the homes do not have a cover on the fuse board and others have had the cover taken off so plug in mcb's can be accomodated. Is this still ok?"
Z.
The problem is as far as I can see, not that everybody would agree, would be the paradox of BS7671 verses the Building control regs where BS7671 is not retrospective as long as the inspector regards the installation to be safe according to the time is was installed and hence maintained and now the building control regs that expect that domestic properties to be designed and installed to the latest regulations, particularly for rental properties.
The breaking capacity of the Wylex plug in MCBs were rated at 1.5kA and 3kA which may not be strong enough to withstand the possible fault currents relying on the service fuse to absorb the enrgy let through.