Number of luminaires on a lighting circuit – new house
Hi,
I am doing a provisional lighting layout for a new house which will use LED lamps throughout. (The final electrical design will be done by the building contractor, but I want to get things right in the design brief  that I give him and want to make sure that I’m not giving him “guidelines” that are not possible to meet.)
The intent is that there will be separate circuits for the ground and first floors, but that additional circuits should not be required. As all of the luminaires will be using low power, mains voltage, LEDs, predominantly downlights, I don’t think there is any concern around exceeding the current capacity of the (1.0 or 1.5mm2) cable and a 6A RCD.
The only issue that I could see is the electrical designer raising is the guidelines in the 2018 On-Site guide in Appendix on Maximum Demand and Diversity. The Appendix is marked as “Guidance Only” but I am concerned that it would be easy for the contactor to just take compliance with it as the easy way out.
Table A1 gives the assumed current demand for a lighting circuit to be 100W per lighting outlet (I guess from when 100W incandescents were the norm), that would be around 12 luminaires or 18 allowing for the diversity in Table A2. (The section does say that “The values given in Table A2, therefore, may be increased or decreased as decided by the installation designer concerned.”)  With LED downlighters everywhere, there will be around 60 luminaires with a load around 300W. (One could take the view that a new owner could replace all the LEDs with 100W fittings, but I think that would be an unreasonable argument.)
Other than arguments around inconvenience should the circuit trip, would it be unreasonable to ask the designer to implement a singe circuit for these loads? (Assuming of course, that the voltage drop was within spec.)
As an aside, is there any reason that external lights could not be on the same RCD protected circuit as the rest of the floor?
Dave
  • You may be confusing fault current and temperature Z, they are not necessarily related at all. A type C or B does not have a difference over SCC, only surges.
  • davezawadi (David Stone):
    Nope, I know the difference between B & C types. I was primarily referring to the fact that a 16 Amp protected circuit can produce much more heat during a fault than a 6 Amp protected circuit.  The B6 M.C.B. will operate more quickly than a 16 Amp. M.C.B. on overload.  The heating effect of a fault current is related to the current magnitude. (I2R heating.) Obviously arcing will produce a varying current so the heating effect will vary.