bonding a short section of water supply pipe

In a victorian terrace house, a lead water supply pipe enters the damp cellar, runs about a meter along the wall to the main brass stopcock, then converts to plastic pipe before exiting the cellar to the rest of the house (which is likely to be a mixture of copper and plastic). The stopcock is a couple of feet away from the CU. Should the supply pipe be bonded? My feeling is no, but I'd be interested in other opinions.


While I'm on the subject, a more general question. Why must any bonding be done after the main stopcock? For example where the supply tees off immediately after the stopcock, is it better to bond one of the tees, or bond just before the stopcock? Where there is a long run of supply pipe before the stopcock, is it better to bond after, with a long MPBC run back to the MET, or bond it near the MET even where that's before the stopcock?
Parents
  • I was pulled up on this once by a meter man, he insisted I changed the bond position on a stop tap coming out of the floor. The only problem was that this was not the main stop tap, it fed the Greenhouse! The main incoming pipe was 2" but wasn't by the meter position and was bonded too. One cannot tell some people.


    In the case of the OP, there is little danger, as most of us don't play with the CU and a water pipe at the same time, but I suppose a couple of feet could be done, so a bond is easier.  As for BS 951 clips on plastic pipes, I found one at a swimming pool once (75mm pipe), blue and all. There was even the safety notice attached. I quizzed the company on why, and they said the incoming water needed to be "discharged". Wonderful.
Reply
  • I was pulled up on this once by a meter man, he insisted I changed the bond position on a stop tap coming out of the floor. The only problem was that this was not the main stop tap, it fed the Greenhouse! The main incoming pipe was 2" but wasn't by the meter position and was bonded too. One cannot tell some people.


    In the case of the OP, there is little danger, as most of us don't play with the CU and a water pipe at the same time, but I suppose a couple of feet could be done, so a bond is easier.  As for BS 951 clips on plastic pipes, I found one at a swimming pool once (75mm pipe), blue and all. There was even the safety notice attached. I quizzed the company on why, and they said the incoming water needed to be "discharged". Wonderful.