The IET is carrying out some important updates between 17-30 April and all of our websites will be view only. For more information, read this Announcement

This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

bonding a short section of water supply pipe

In a victorian terrace house, a lead water supply pipe enters the damp cellar, runs about a meter along the wall to the main brass stopcock, then converts to plastic pipe before exiting the cellar to the rest of the house (which is likely to be a mixture of copper and plastic). The stopcock is a couple of feet away from the CU. Should the supply pipe be bonded? My feeling is no, but I'd be interested in other opinions.


While I'm on the subject, a more general question. Why must any bonding be done after the main stopcock? For example where the supply tees off immediately after the stopcock, is it better to bond one of the tees, or bond just before the stopcock? Where there is a long run of supply pipe before the stopcock, is it better to bond after, with a long MPBC run back to the MET, or bond it near the MET even where that's before the stopcock?
Parents
  • geoffsd:


    Also - the stop-cock is irrelevant and is mentioned nowhere in the regulations.


    Correct it doesn't say 'Stop-Cock' but 544.1.2 does say the connection shall be made to the consumer's pipework.  Where this starts is at the output of the meter for Gas.  For water it's a bit more arguable as if there is an external stop tap then all the pipework from there is the Consumer's responsibility, according to the water company so the internal stop cock may then be inserted in the consumer's pipework, and may not be the demarcation point.


Reply
  • geoffsd:


    Also - the stop-cock is irrelevant and is mentioned nowhere in the regulations.


    Correct it doesn't say 'Stop-Cock' but 544.1.2 does say the connection shall be made to the consumer's pipework.  Where this starts is at the output of the meter for Gas.  For water it's a bit more arguable as if there is an external stop tap then all the pipework from there is the Consumer's responsibility, according to the water company so the internal stop cock may then be inserted in the consumer's pipework, and may not be the demarcation point.


Children
No Data