mapj1:
Why do we worry about current in a lead sheath more or less than in a steel armour on a modern cable ? - if anything the lead has a larger cross-section, is better cooled due the larger surface area and and if anything paper and oil not exposed to air is likely to be more robust than XPLE insulation in terms of failure modes if it heats up.
I agree once the lead is damaged or not connected, then you have a problem, but that is true of any armoured cable.
Mike.
One of my concerns about using lead is its low melting point, perhaps when carrying large fault currents. Domestic lead covered cables of old were perhaps fused at 5, 15 or even 30 Amps so fault currents were relatively small. With lead pipes that may carry large diverted neutral currents the lead may melt or or best become soft, so fitting a B.S. 951 earth clamp to a lead gas pipe could be dangerous. I would never do so. Lead melts at about 300 degrees C and copper at over 1,000 degrees C.
Back in the 40s a device called a "Pyrotip" was used to "Burn" lead for jointing. The manufacturer was the General Electric Company of Schenectady. The heating source was electrical in the form of a step down transformer to a carbon electrode. The work was connected by a clamp to one terminal and the carbon rod to the other. The p.d. was insufficient to form an arc. The lead was melted only by the power dissipated in the carbon rod and that dissipated in the contact resistance between rod and work.
So in this case electricity traveling through the rod and lead, was a friend to melting lead, in other cases I am concerned about gas leaking from damaged lead pipes.
Z.
mapj1:
Why do we worry about current in a lead sheath more or less than in a steel armour on a modern cable ? - if anything the lead has a larger cross-section, is better cooled due the larger surface area and and if anything paper and oil not exposed to air is likely to be more robust than XPLE insulation in terms of failure modes if it heats up.
I agree once the lead is damaged or not connected, then you have a problem, but that is true of any armoured cable.
Mike.
One of my concerns about using lead is its low melting point, perhaps when carrying large fault currents. Domestic lead covered cables of old were perhaps fused at 5, 15 or even 30 Amps so fault currents were relatively small. With lead pipes that may carry large diverted neutral currents the lead may melt or or best become soft, so fitting a B.S. 951 earth clamp to a lead gas pipe could be dangerous. I would never do so. Lead melts at about 300 degrees C and copper at over 1,000 degrees C.
Back in the 40s a device called a "Pyrotip" was used to "Burn" lead for jointing. The manufacturer was the General Electric Company of Schenectady. The heating source was electrical in the form of a step down transformer to a carbon electrode. The work was connected by a clamp to one terminal and the carbon rod to the other. The p.d. was insufficient to form an arc. The lead was melted only by the power dissipated in the carbon rod and that dissipated in the contact resistance between rod and work.
So in this case electricity traveling through the rod and lead, was a friend to melting lead, in other cases I am concerned about gas leaking from damaged lead pipes.
Z.