bonding a short section of water supply pipe

In a victorian terrace house, a lead water supply pipe enters the damp cellar, runs about a meter along the wall to the main brass stopcock, then converts to plastic pipe before exiting the cellar to the rest of the house (which is likely to be a mixture of copper and plastic). The stopcock is a couple of feet away from the CU. Should the supply pipe be bonded? My feeling is no, but I'd be interested in other opinions.


While I'm on the subject, a more general question. Why must any bonding be done after the main stopcock? For example where the supply tees off immediately after the stopcock, is it better to bond one of the tees, or bond just before the stopcock? Where there is a long run of supply pipe before the stopcock, is it better to bond after, with a long MPBC run back to the MET, or bond it near the MET even where that's before the stopcock?
Parents
  • AJJewsbury:
    Compression fitting can be used on coppe



    Besides if it was at all credible that you had enough current flowing through the bonding to get the pipework to hundreds of degrees - what state would the 10mm² bonding conductor be in? (even thin walled 15mm copper pipe has a copper c.s.a of around 30mm² - lead pipes have a lot more metal that likely makes up for its higher resistance)


       - Andy.


    So now you have worried me even more with talk of very hot bonding cables Andy. I suppose that they could get very hot in certain areas of towns or cities. The requirements for so large a bonding cable shows just how large potential fault currents could be. Worrying! And to think that back in the 70s I believe that the specifications were for smaller sized bonding cables.


    Z.


Reply
  • AJJewsbury:
    Compression fitting can be used on coppe



    Besides if it was at all credible that you had enough current flowing through the bonding to get the pipework to hundreds of degrees - what state would the 10mm² bonding conductor be in? (even thin walled 15mm copper pipe has a copper c.s.a of around 30mm² - lead pipes have a lot more metal that likely makes up for its higher resistance)


       - Andy.


    So now you have worried me even more with talk of very hot bonding cables Andy. I suppose that they could get very hot in certain areas of towns or cities. The requirements for so large a bonding cable shows just how large potential fault currents could be. Worrying! And to think that back in the 70s I believe that the specifications were for smaller sized bonding cables.


    Z.