AJJewsbury:Compression fitting can be used on coppe
Besides if it was at all credible that you had enough current flowing through the bonding to get the pipework to hundreds of degrees - what state would the 10mm² bonding conductor be in? (even thin walled 15mm copper pipe has a copper c.s.a of around 30mm² - lead pipes have a lot more metal that likely makes up for its higher resistance)
- Andy.
So now you have worried me even more with talk of very hot bonding cables Andy. I suppose that they could get very hot in certain areas of towns or cities. The requirements for so large a bonding cable shows just how large potential fault currents could be. Worrying! And to think that back in the 70s I believe that the specifications were for smaller sized bonding cables.
Z.
AJJewsbury:Compression fitting can be used on coppe
Besides if it was at all credible that you had enough current flowing through the bonding to get the pipework to hundreds of degrees - what state would the 10mm² bonding conductor be in? (even thin walled 15mm copper pipe has a copper c.s.a of around 30mm² - lead pipes have a lot more metal that likely makes up for its higher resistance)
- Andy.
So now you have worried me even more with talk of very hot bonding cables Andy. I suppose that they could get very hot in certain areas of towns or cities. The requirements for so large a bonding cable shows just how large potential fault currents could be. Worrying! And to think that back in the 70s I believe that the specifications were for smaller sized bonding cables.
Z.