I reckon the reference in the regulations to hard pipework is more to avoid the flexible corrugated pipes you now often see on gas meters these days.
- Andy.
Then if the regs. are referring to a flexible pipe they should use the word "flexible." or "non rigid". No, the regulation says "hard", The opposite is not flexible but soft..
If it was a gas pipe there is NO WAY that I would apply a bonding clamp on it. Lead melts at the low relatively temperature of about 330 degrees C. A nice big diverted neutral current could cause a house explosion. No, hard metal means iron or steel or copper.
LOOK. Cooking with lead........
Melting Lead On A Stove - Bing video
Z.
wallywombat:
Note that the damp cellar walls and floor are likely to be at a similar potential to the lead pipe (and to the general mass of earth surrounding the cellar).
I would not want to fix a clamp onto soft lead.
geoffsd:
Also - the stop-cock is irrelevant and is mentioned nowhere in the regulations.
Correct it doesn't say 'Stop-Cock' but 544.1.2 does say the connection shall be made to the consumer's pipework. Where this starts is at the output of the meter for Gas. For water it's a bit more arguable as if there is an external stop tap then all the pipework from there is the Consumer's responsibility, according to the water company so the internal stop cock may then be inserted in the consumer's pipework, and may not be the demarcation point.
Alcomax:
But it is a damp cellar, probably victorian brick floor or flagstones. What happens if you are barefoot, checking the stop tap and that lead pipe imports a fault from next door? Ok, a reason for being barefoot; you were just having a shower and the water went off, so you amble down to find out what is going on. Or forget barefoot; the CU is metal and readily accessible with the lead pipe.
Just cover the water pipe with electrically insulating material, or box it in, then it can't be touched. Out of sight and out of mind, and all that jazz.
Z.