davezawadi (David Stone):
Ridiculous! Copper is softer than Lead Z, particularly if recently annealed. So I assume you don't bond copper pipes either, particularly as they are much thinner walled? The diverted N current to melt a 1" gas pipe would need to be several hundred Amps to melt it!
The copper versus lead hardness table.
https://en.wikipedia.org/wiki/Hardnesses_of_the_elements_(data_page)
Z.
When?
AJJewsbury:Notice in this clip that jointing involves molten lead
It'll be solder rather than lead (a lead alloy, but with a much lower melting point).
- Andy.
That's presumably why the earth wire was mechanically attached reliably before soldering, so that it was not relying upon just the solder.
Z
AJJewsbury:When?
When these diverted N currents you're worrying about are trying to make their way back to the star point. They're just as likely to try and get there via the lead sheath of a cable than a gas pipe (probably more so these days as most gas mains have been replaced by plastic).
BTW around here most earths are connected to the lead sheath by a pipe clip of some kind - the old YEB didn't seem to like hot works and appeared have their own not quite BS 951 variant. There's loads of PILC still in service (often upraded to 80A or 100A fuses too).
- Andy.
The diverted neutral currents can be conducted by the armour of the P.I.L.C. cable.
For a domestic P.I.L.C. service cable, the earth fault currents will be limited in size by the protective device, say a 30 Amp fuse wire. So the lead will not have to carry hundreds of Amps. as it may for a lead gas pipe.
IET Forums - PILC Earth Clamp (theiet.org)
Z.
davezawadi (David Stone):
Whilst those numbers are correct for Brinell hardness they do not really relate to the case. They are obtained by pressing a 4 sided diamond into a thick block of the material with a known load and measuring the depression. The reason I said that annealed copper was softer is that the thin sections used in pipes behave by deflection not much dependant on the hardness, but the material modulus. A BS951 clamp cannot apply enough force to deform a lead gas pipe (about 4-5mm wall) very much, whereas a 0.8mm thick copper one (particularly if soft annealed like microbore pipes or well heated and cooled larger ones). The clamp itself is designed to spread the clamping force around much of the pipe diameter, and generally prevents very much deformation of the circular shape which is inherently very strong (think of bridge arches). I think your fears are groundless, but you may care to try it one day when you find an odd bit of lead (although often a harder alloy called compo in times past) pipe. The wide ranges of the number for Brinell hardness are caused by the wide range of tempers of the material, depending on mechanical and heat treatments before you get it. Take aluminium alloys, for example, T6016 which is used for many purposes including aircraft. Its strength (or stiffness) can be varied across a wide range by heat treatment, the strongest and stiffest being T6016-T6. The same annealed correctly is very soft and easily bent, the -T6 is very stiff indeed. Neither copper or lead pipe will be punctured by mechanical deformation unless very severe, the copper being the most susceptible because it work hardens and becomes brittle.
I did read some time ago about an apprentice that tightened a B.S. 951 earthing clamp on a copper pipe so tight that he punctured the water pipe.
Z.