mapj1:
Why do we worry about current in a lead sheath more or less than in a steel armour on a modern cable ? - if anything the lead has a larger cross-section, is better cooled due the larger surface area...
This American video confirms the robustness of P.I.L.C. cables.
https://www.bing.com/videos/search?q=youtube+terminating+PILC+lead+cable&docid=608021297359238224&mid=2B0334B9E1D44F83AB9D2B0334B9E1D44F83AB9D&view=detail&FORM=VIRE
One of my concerns about using lead is its low melting point, perhaps when carrying large fault currents. Domestic lead covered cables of old were perhaps fused at 5, 15 or even 30 Amps so fault currents were relatively small. With lead pipes that may carry large diverted neutral currents the lead may melt or or best become soft, so fitting a B.S. 951 earth clamp to a lead gas pipe could be dangerous. I would never do so. Lead melts at about 300 degrees C and copper at over 1,000 degrees C.
AJJewsbury:One of my concerns about using lead is its low melting point, perhaps when carrying large fault currents. Domestic lead covered cables of old were perhaps fused at 5, 15 or even 30 Amps so fault currents were relatively small. With lead pipes that may carry large diverted neutral currents the lead may melt or or best become soft, so fitting a B.S. 951 earth clamp to a lead gas pipe could be dangerous. I would never do so. Lead melts at about 300 degrees C and copper at over 1,000 degrees C.
I'm sure you're worrying over nothing. Copper pipework is no more resistant to heat than lead pipework - as both will fail well below 300 degrees when the solder in the joints melts. If it's not an issue with copper pipes why should it be with lead ones?
Blowlamp flame on copper pipe: pipe remains intact.
Blowlamp flame on lead pipe and it will melt.
Compression fitting can be used on copper pipe and no solder is required.
Are you really suggesting that if you worked on an installation where all the gas pipework was all lead, you'd leave it unbonded?
I don't think that an all lead gas pipe system in a house would comply with modern gas regs. these days Andy.
What I said was that I would not fit a B.S. 951 earthing clamp onto a lead gas pipe. Nothing more nor less.
Zoomup:
What does the Standard have to say about the types of pipe that may be used? (I have not got a copy and have lost my library access for the time being.)
AJJewsbury:Compression fitting can be used on copper pipe and no solder is required.
In theory perhaps, in practice copper gas pipes are soldered (other than for the final joint for an appliance). So really lead pipework in no worse than copper - the solder is still the weak link in both systems you're likely to find in the real world.
Have you ever noticed the large nuts on the gas pipes at the gas meter Andy?