Number of appliances on one radial line

Former Community Member
Former Community Member
Hello all,  I would really like some advice/reassurance.  We are having our kitchen done and the existing wiring is a radial line.  The builders are installing a 2.5mm TE line which services a double socket (coffee machine), dishwasher, boiling water tap and washer dryer.


My concern is that a single radial line is insufficient for the loading s involved.


I would really appreciate your thoughts.

Parents
  • A 20 amp circuit is almost certainly fine for the loads as described, I would however consider a 32 amp circuit to be better practice so as to allow for any extra appliances that may be added in future.
Reply
  • A 20 amp circuit is almost certainly fine for the loads as described, I would however consider a 32 amp circuit to be better practice so as to allow for any extra appliances that may be added in future.