Number of appliances on one radial line

Former Community Member
Former Community Member
Hello all,  I would really like some advice/reassurance.  We are having our kitchen done and the existing wiring is a radial line.  The builders are installing a 2.5mm TE line which services a double socket (coffee machine), dishwasher, boiling water tap and washer dryer.


My concern is that a single radial line is insufficient for the loading s involved.


I would really appreciate your thoughts.

Parents
  • SVHomeowner:

    Thanks for all the advice guys.  Something related... builder has said he’s going to use the existing 10mm cable to power double oven (5.2kw) and induction hob (7.2kw) on a 45A mcd, is that ok?


    Looks fine to me - by the usual calculation a normal 32A circuit would be plenty. Just as long as the manufacturer's instructions don't demand lower rated protective devices.

       - Andy.


Reply
  • SVHomeowner:

    Thanks for all the advice guys.  Something related... builder has said he’s going to use the existing 10mm cable to power double oven (5.2kw) and induction hob (7.2kw) on a 45A mcd, is that ok?


    Looks fine to me - by the usual calculation a normal 32A circuit would be plenty. Just as long as the manufacturer's instructions don't demand lower rated protective devices.

       - Andy.