Looping Lighting feeds at switches in singles

Hi

A few months back I posted a question regarding different methods of connecting lighting feeds and switch feeds at switches in singles conduit cable. My question was more from an eddy current perspective. I’m currently working on a job with steel trunking where the drops to switches and sockets etc from the steel trunking are in plastic conduit and the switches / sockets are plastic. My previous post queried whether having just live / switch live and earth down through a single hole in the trunking to the switch or live/neutral/earth supply to switch and live/neutral/earth out to the light through a single hole in the steel trunking was acceptable. I opted for the latter. My question now is can I take a permanent feed to the next switch from the previous switch? In effect I’ll have l/n/e supply to switch and l/n/e to the light and l/n/e to the next switch, so 9 cables at the switch position all through a single hole in the steel trunking. I know this method is used in domestic settings with t&e cable but singles in conduit has the flexibility of running each single cable directly where it needs to go but from an eddy current perspective having all my single cables through the single hole in the metal trunking down to the switch gives me peace of mind. Thanks in advance
Parents
  • AJJewsbury:
    Having the live feed to a switch, and the switched live from the switch to the lamp passing through a single hole or conduit is fine. The current "goes" along one wire and "returns" along the other, thereby producing no significant magnetic fields or eddy currents.

    And the same for N when it's looped at the light (the traditional way with conduit is to loop L at the switch and loop N at the light) - as long as all the wires to any accessory pass through the same hole/conduit, then the currents must balance - as there's nowhere else for any of it to go.

       - Andy.


    Andy

    I know the traditional method with conduit and singles is to loop the neutral at the light but my example of 9 wires ( l/n/e feed to switch position , joining neutrals and earths in the switch box, l/n/e switch feed to light and l/n/e loop feed to next switch through one hole in the metal trunking is also acceptable? Just to clarify the conduit and switch is plastic but the trunking is metal.


    Thanks


Reply
  • AJJewsbury:
    Having the live feed to a switch, and the switched live from the switch to the lamp passing through a single hole or conduit is fine. The current "goes" along one wire and "returns" along the other, thereby producing no significant magnetic fields or eddy currents.

    And the same for N when it's looped at the light (the traditional way with conduit is to loop L at the switch and loop N at the light) - as long as all the wires to any accessory pass through the same hole/conduit, then the currents must balance - as there's nowhere else for any of it to go.

       - Andy.


    Andy

    I know the traditional method with conduit and singles is to loop the neutral at the light but my example of 9 wires ( l/n/e feed to switch position , joining neutrals and earths in the switch box, l/n/e switch feed to light and l/n/e loop feed to next switch through one hole in the metal trunking is also acceptable? Just to clarify the conduit and switch is plastic but the trunking is metal.


    Thanks