AJJewsbury:Should a time delayed 100mA type be used? The Guidance note says that the 100 mA R.C.D. is chosen to discriminate with the pitch socket outlets R.C.D.s
Yes - you always need timedelay on any upstream RCD to achieve discrimination - as Reg 536.4.1.4 etc. tries to say (but probably with far too many words).
To my mind the ratio of the residual ratings should ideally be 3:1 not to highest rated downstream device, but to the sum of the downstream devices.
- Andy.
So, the Fig. 7.1 illustration should have the words "Time delayed" added to the 100 mA R.C.D. that supplies 4 caravans, in Guidance Note 7, Special Locations.