Sparkingchip:
If you did a 5x test and sent 150 mA to earth without tripping the the upfront RCD then as Bod says it’s either time delayed or faulty, alternatively it is 300 mA, an ELCB or doesn’t exist.
A 30 mA test will often take 100 mA RCD out if it’s not time delayed and the test button on the 30 mA RCD can take both of them out.
The tests were a 1/2 and 1X test, as I wanted to lessen the risk of taking out the inaccessible R.C.D., if there is one, in the locked brick supply shed. I was more interested in checking over sensitive R.C.D.s at the van hook up and inside the van. They both tested o.k. for functionality.
Sparkingchip:
If you did a 5x test and sent 150 mA to earth without tripping the the upfront RCD then as Bod says it’s either time delayed or faulty, alternatively it is 300 mA, an ELCB or doesn’t exist.
A 30 mA test will often take 100 mA RCD out if it’s not time delayed and the test button on the 30 mA RCD can take both of them out.
The tests were a 1/2 and 1X test, as I wanted to lessen the risk of taking out the inaccessible R.C.D., if there is one, in the locked brick supply shed. I was more interested in checking over sensitive R.C.D.s at the van hook up and inside the van. They both tested o.k. for functionality.