perspicacious:
I'm going for 500 mA RCD in there Andy!
Regards
BOD
Quite possibly, I tried it at 30 mA and 150 mm without getting it to trip, so I fitted a double pole B40/30 mA RCBO to the shower circuit and wrote an advisory note.
It is earthed TNCS-PME.
perspicacious:
I'm going for 500 mA RCD in there Andy!
Regards
BOD
Quite possibly, I tried it at 30 mA and 150 mm without getting it to trip, so I fitted a double pole B40/30 mA RCBO to the shower circuit and wrote an advisory note.
It is earthed TNCS-PME.