The IET is carrying out some important updates between 17-30 April and all of our websites will be view only. For more information, read this Announcement

This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Static Caravan Problems.

I was called out to a static holiday/residential caravan today. Nuisance tripping was reported. Apparently the electrics were reliable before the van was moved to a new pitch on the same sandy site. The van's consumer unit comprises 1 30mA R.C.D., a 32 Amp socket M.C.B. and a 6A lighting M.C.B.


The pitch permanent "hook up" point comprises a 30 mA R.C.D. and a 16 Amp M.C.B.


The lady has many high powered appliances, 2kW kettle, three 2kW+ room heaters, a 2.2kW coffee machine etc. The heating is normally by bottled gas.


The two R.C.D.s tested out fine, not over sensitive. But the van owner can not remember which devices tripped off over a period of time. Once the nearby brick supply building had to be accessed to reset something, but we were not allowed even just to look inside it today by the site owners. Very unhelpful.


Anyway, all appliances tested good, no faults. I presumed that the lady had plugged too many items in at once.                                                                                                                                                                                                                                                                Guidance note 7, page 58 Fig. 7.1 it shows 4 possible separate vans being supplied via a single  100 mA R.C.D.


So, looking at the possibility of nuisance tripping if 4 vans each leak say 20 to 30 mA, the 100 mA R.C.D. could trip off blacking them all out. Should a time delayed 100mA type be used? The Guidance note says that the 100 mA R.C.D. is chosen to discriminate with the pitch socket outlets R.C.D.s. But, if say 100mA was to flow from a van fault,  both the 30mA pitch socket R.C.D. AND the 100mA brick supply building could trip off together. This would then deprive a total of 4 vans of a supply.


Comments please.


Thanks,


Z.


Parents
  • Sparkingchip:
    91f336dee0d852dcea5c7e59286acdea-original-20200728_110719.jpg


    One in South Wales from last year I posted a picture of before on this forum. 


    The label on it says it’s a 0.5 amp RCD, just as Bod said.



    If I saw something like that not sure ide know what to make of it thinking about it is it just a very large version of what you'd find in a normal 30mA RCD I've never seen anything like that before

     


     


Reply
  • Sparkingchip:
    91f336dee0d852dcea5c7e59286acdea-original-20200728_110719.jpg


    One in South Wales from last year I posted a picture of before on this forum. 


    The label on it says it’s a 0.5 amp RCD, just as Bod said.



    If I saw something like that not sure ide know what to make of it thinking about it is it just a very large version of what you'd find in a normal 30mA RCD I've never seen anything like that before

     


     


Children
No Data