This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

BIG BIG Range Cooker.

I wired up a big range cooker today in a new house. 14kW ish. A 32 Amp 6.0mm2 circuit. Final meter of T&E in 4.0mm2. The big worry is that we could not find a cooker switch on the wall anywhere, just the cooker connection plate. Perhaps not needed by the Regs. nowadays, but nice to turn off when cleaning the cooker, servicing it or in case of emergency, or last thing at night to stop children fiddling.


I warned the owner that it is not a good idea to turn on all ovens and hobs at once.


Z.
Parents
  • Most manufacturers add up the total of the elements, regardless of whether they can be all energised simultaneously. I would have used 6mm2 t&e to the cooker though, rather than choosing 4. 


    Regards,


    Alan.
Reply
  • Most manufacturers add up the total of the elements, regardless of whether they can be all energised simultaneously. I would have used 6mm2 t&e to the cooker though, rather than choosing 4. 


    Regards,


    Alan.
Children
No Data