P.M.E. and a Broken Neutral.

Nowt ont box? Then try this to challenge the mind.

Podcast 77: Earthing pt 3, Hazards and Neutral Current Diversion - Bing video


Z.
Parents


  • It is customary to make some reference, page 44 IET Guidance Note 8. So there are two basic forms of TN-C-S systems: TN-C-S system with PME and TN-C-S system with PMB.

    Fig 4.9 shows the PNB earth neutral link can be done at the installation end and I have seen this at main switchboards with a 11KV/400Vtransformer not far away outside. The problem with this is (If there is a problem) with a three phase supply (single phase as well ) if overhead wiring is divided up among a number of dwellings is that on a unbalanced load there is a current flowing in the neutral , (could be large) and this the conductor we are connecting the earth to.

    Quarries: Someone said Quarries now come under BS7671 after about 30 40years having there own statutory regulations and having before regulation earth conduction must be at least 50% of line conduction. It is incomprehensible to think that you could apply BS7671 to quarries fixed or portable plant and comply.   


    The Types Of Earthing System as showing on the inspection form.

    BS 7671 defines four types of earthing system:

    a) TN-S

    b) TN-C-S

    c) TT

    d) IT.

    Where above apply to quarries where PME is not allowed, I would say PMB, where is the tick box.

    Below is where PME is not allowed; (reference from any one of the supply providers)


    1 Installations Where A PME Earth Terminal Shall Not Be Offered

    NOTE: In certain cases, although parts of an installation may be prohibited from

    use of a PME Earth Terminal (e.g. Caravan or Boat) other parts may not (e.g.

    permanent buildings at Caravan Park, Camping Park or Marina). This section

    shall be read in conjunction with 4.2.2.

    PME shall not be offered if this would allow the connection of the PME Earth

    Terminal to any metalwork of the following:

    a) Caravan. However, see 4.2.2.1 for Caravan Parks/Camping Parks.

    b) Fairground, Amusement Park and Circus Temporary Electrical Installations

    for Structures, Amusement Devices and Booths.

    c) Mobile Home/Residential Park Home if specific conditions apply making it

    effectively equivalent to a Caravan. See 4.2.2.1 for Mobile Home Parks.

    d) Boat, Houseboat or Boat Mooring Supply. However, see 4.2.2.5 for Marinas

    and similar locations.

    e) Outdoor Amenity Showers and Outdoor Amenity Facilities.

    f) Fuel Filling Station. However, see 4.2.2.6 for Motorway Services Premises

    and similar locations adjacent to Fuel Filling Stations. Areas where

    dangerous/explosive substances are stored are treated in the same way as a

    Fuel Filling Station.

    g) Mine Underground Shaft. However, see 4.2.2.8 for Mine permanent

    buildings.

    h) Quarry Production Area. However, see 4.2.2.9 for Quarry permanent

    buildings.

    i) Construction Site or Demolition Site. However, see 4.2.2.7 for Construction

    Site permanent buildings.

    j) Multiple Occupancy Buildings, including flats, maisonettes, bed-sits,

    industrial units and commercial premises in Multiple Occupancy Buildings.

    See ST:SD5C.

    k) Shared communication towers.

    l) Impressed Current Cathodic Protection Systems.

    m) An AC electrified railway/tramway, including traction supply point

    substations

    , train stations, signals, level crossings, point heaters and the like.

    However, see 4.2.2.13 for LV supplies to DC electrified and non-electrified

    railways/tramways, and 4.2.2.13 for details.

    n) Mobile phone base stations with antennae on HV towers. See ST:SD6E.

    o) Direct supply to a Solar PV System (i.e. solar farm).

    Note: Quarries I no longer now electrical  inspect, but still remember the stress.

    Please no hostility towards my post

    regards

    JCM

Reply


  • It is customary to make some reference, page 44 IET Guidance Note 8. So there are two basic forms of TN-C-S systems: TN-C-S system with PME and TN-C-S system with PMB.

    Fig 4.9 shows the PNB earth neutral link can be done at the installation end and I have seen this at main switchboards with a 11KV/400Vtransformer not far away outside. The problem with this is (If there is a problem) with a three phase supply (single phase as well ) if overhead wiring is divided up among a number of dwellings is that on a unbalanced load there is a current flowing in the neutral , (could be large) and this the conductor we are connecting the earth to.

    Quarries: Someone said Quarries now come under BS7671 after about 30 40years having there own statutory regulations and having before regulation earth conduction must be at least 50% of line conduction. It is incomprehensible to think that you could apply BS7671 to quarries fixed or portable plant and comply.   


    The Types Of Earthing System as showing on the inspection form.

    BS 7671 defines four types of earthing system:

    a) TN-S

    b) TN-C-S

    c) TT

    d) IT.

    Where above apply to quarries where PME is not allowed, I would say PMB, where is the tick box.

    Below is where PME is not allowed; (reference from any one of the supply providers)


    1 Installations Where A PME Earth Terminal Shall Not Be Offered

    NOTE: In certain cases, although parts of an installation may be prohibited from

    use of a PME Earth Terminal (e.g. Caravan or Boat) other parts may not (e.g.

    permanent buildings at Caravan Park, Camping Park or Marina). This section

    shall be read in conjunction with 4.2.2.

    PME shall not be offered if this would allow the connection of the PME Earth

    Terminal to any metalwork of the following:

    a) Caravan. However, see 4.2.2.1 for Caravan Parks/Camping Parks.

    b) Fairground, Amusement Park and Circus Temporary Electrical Installations

    for Structures, Amusement Devices and Booths.

    c) Mobile Home/Residential Park Home if specific conditions apply making it

    effectively equivalent to a Caravan. See 4.2.2.1 for Mobile Home Parks.

    d) Boat, Houseboat or Boat Mooring Supply. However, see 4.2.2.5 for Marinas

    and similar locations.

    e) Outdoor Amenity Showers and Outdoor Amenity Facilities.

    f) Fuel Filling Station. However, see 4.2.2.6 for Motorway Services Premises

    and similar locations adjacent to Fuel Filling Stations. Areas where

    dangerous/explosive substances are stored are treated in the same way as a

    Fuel Filling Station.

    g) Mine Underground Shaft. However, see 4.2.2.8 for Mine permanent

    buildings.

    h) Quarry Production Area. However, see 4.2.2.9 for Quarry permanent

    buildings.

    i) Construction Site or Demolition Site. However, see 4.2.2.7 for Construction

    Site permanent buildings.

    j) Multiple Occupancy Buildings, including flats, maisonettes, bed-sits,

    industrial units and commercial premises in Multiple Occupancy Buildings.

    See ST:SD5C.

    k) Shared communication towers.

    l) Impressed Current Cathodic Protection Systems.

    m) An AC electrified railway/tramway, including traction supply point

    substations

    , train stations, signals, level crossings, point heaters and the like.

    However, see 4.2.2.13 for LV supplies to DC electrified and non-electrified

    railways/tramways, and 4.2.2.13 for details.

    n) Mobile phone base stations with antennae on HV towers. See ST:SD6E.

    o) Direct supply to a Solar PV System (i.e. solar farm).

    Note: Quarries I no longer now electrical  inspect, but still remember the stress.

    Please no hostility towards my post

    regards

    JCM