geoffsd:Table 4D2 6mm clipped direct says 46A, continuous rating. A 10.5kW shower takes 45.65A on 230V so is quite satisfactory on the 6mm cable.
4D5 (T&E) states 47A.
The 10.5kW will more than likely be stated for 240V so 43.8A (42A @ 230V).
Yes, but only for ref. method C (Clipped direct). Other methods shown in Table 4D5 show much lower current ratings.
Z.
geoffsd:Table 4D2 6mm clipped direct says 46A, continuous rating. A 10.5kW shower takes 45.65A on 230V so is quite satisfactory on the 6mm cable.
4D5 (T&E) states 47A.
The 10.5kW will more than likely be stated for 240V so 43.8A (42A @ 230V).
Yes, but only for ref. method C (Clipped direct). Other methods shown in Table 4D5 show much lower current ratings.
Z.