Farmboy:AJJewsbury:Clipped direct includes cables installed on brick walls with or without capping covered in plaster
Indeed. On the other hand most shower cables run through a floor void at some point - that's method B - now what does a 6mm² look like?
- Andy.
Will 'cable installed in a ceiling' in section 7.2 of Apdx 4 also apply if there's no junction box, just the cable in the ceiling, that refers to RM A?
I believe that the junction box heat concerns apply to heat created by a luminaire, such as a tungsten filament lamp. Sometimes a junction box was situated close to or by a hot luminaire.
Table 4D5 is for use with cables at 30 degrees C ambient temp. and conductor operating temp. of 70 degrees C. You could warm your hands on a winter's day at 70 degrees C. The old fashioned big brown circular junction boxes that I use won't be adversely affected by a warm environment or catch fire.
Z.
Farmboy:AJJewsbury:Clipped direct includes cables installed on brick walls with or without capping covered in plaster
Indeed. On the other hand most shower cables run through a floor void at some point - that's method B - now what does a 6mm² look like?
- Andy.
Will 'cable installed in a ceiling' in section 7.2 of Apdx 4 also apply if there's no junction box, just the cable in the ceiling, that refers to RM A?
I believe that the junction box heat concerns apply to heat created by a luminaire, such as a tungsten filament lamp. Sometimes a junction box was situated close to or by a hot luminaire.
Table 4D5 is for use with cables at 30 degrees C ambient temp. and conductor operating temp. of 70 degrees C. You could warm your hands on a winter's day at 70 degrees C. The old fashioned big brown circular junction boxes that I use won't be adversely affected by a warm environment or catch fire.
Z.