OlympusMons:
Farmboy and Dave, you both mention RM A in your posts when i think you mean RM C. RM A refers to cables in conduit in an insulated walls (and architraves & windowframes). I agree it should be RM C in most ceiling voids.
I did remedials on an EICR recently and the cable type on the schedule of test results was given for all circuits as "A", as was the reference method. I was searching everywhere for cables in an insulated wall, especially near the CU since all circuits were classed as RM A, could't find any insulation. It was the same situation as Dave has, 6mm T&E, 8.5KW shower on a 40A MCB. The inspector C2ed it and recommended putting a 32A mcb in instead, "over-sized over current protective device".
I was referring to section 7.2 in regs appendix 4, page 384, which suggests RM A for 'cables installed in a ceiling', due to possible rise in temperature in JBs . So what I was trying to determine was should a cable in a ceiling void be considered as RM A even when no JBs are present, as the cables could still be subjected to the raised temperature?
OlympusMons:
Farmboy and Dave, you both mention RM A in your posts when i think you mean RM C. RM A refers to cables in conduit in an insulated walls (and architraves & windowframes). I agree it should be RM C in most ceiling voids.
I did remedials on an EICR recently and the cable type on the schedule of test results was given for all circuits as "A", as was the reference method. I was searching everywhere for cables in an insulated wall, especially near the CU since all circuits were classed as RM A, could't find any insulation. It was the same situation as Dave has, 6mm T&E, 8.5KW shower on a 40A MCB. The inspector C2ed it and recommended putting a 32A mcb in instead, "over-sized over current protective device".
I was referring to section 7.2 in regs appendix 4, page 384, which suggests RM A for 'cables installed in a ceiling', due to possible rise in temperature in JBs . So what I was trying to determine was should a cable in a ceiling void be considered as RM A even when no JBs are present, as the cables could still be subjected to the raised temperature?