wallywombat:
In terms of power loss:
If my back-of-the-envelope sums are right, a 15m run of cable for a 45A shower will give 1.7% power losses for 6mm2 and 1% for 10mm2. The larger cable will cost an extra £10 approx, so will pay for itself after about 70 kWh of reduced losses, or 10,000 kWh of shower usage, or about 1000 hours of use. Not sure what that is in units of Teenage Daughters.
I get slightly more. The difference in resistance between the two cable sizes is 4.05 mΩ/m so 61 mΩ. Power = I²R = 123 W extra. For a 15 min shower, that is 1/8 x 1/4 = 1/32 kWh. At 16 p that is a ha'penny per shower, so pay back is after 2000 showers or about 2 years for a hygienic family of three.
wallywombat:
In terms of power loss:
If my back-of-the-envelope sums are right, a 15m run of cable for a 45A shower will give 1.7% power losses for 6mm2 and 1% for 10mm2. The larger cable will cost an extra £10 approx, so will pay for itself after about 70 kWh of reduced losses, or 10,000 kWh of shower usage, or about 1000 hours of use. Not sure what that is in units of Teenage Daughters.