Can i fit a plastic switch fuse such as an 800kmf in the external meter box or does it have to be metal.   I am not interested in the dno view, they always seem to be happy with our switch gear in there around here so long as we leave them enough room.



Gary
Parents
  • "It is not manufactured as an assembly to BS EN 61439-3 as it is not a consumer unit "



    Interesting - I thought most would have considered a switchfuse as coming under the heading of 'similar swicthgear' - being pretty much identical in function to a 1-way CU (DP incomer, feeding one OPD, suitable for use at the origin of an installation and so on).



    Like a shark AJ ?


    It , the KMF, is not manufactured as an assembly to BS EN61439-3, as it is not a consumer unit.


    However, if there is only a KMF and no consumer unit- unlikely- then the intended use changes and would not be in the spirit of 421 etc.


    There are no steel moulded 800KMFs; though there briefly was, though to what BS is lost in time.


    Some may chose to manufacture a switch fuse to 61439-3, as opposed to the specific KMF.


    In the KMF, you cannot change the fuse holder. It is all in a moulded assembly. You could change the fuse, but that is not resetting a device as you would in a consumer unit. For most intended use the KMF is providing HRC fuse  protection usually upstream of a DBO  in a domestic. It is usually not touched by ordinary persons; they would be accessing the consumer unit. The KMF is just a bigger, beefier device than your 13 amp switch fuse connection unit and we do not usually require those to be steel.
Reply
  • "It is not manufactured as an assembly to BS EN 61439-3 as it is not a consumer unit "



    Interesting - I thought most would have considered a switchfuse as coming under the heading of 'similar swicthgear' - being pretty much identical in function to a 1-way CU (DP incomer, feeding one OPD, suitable for use at the origin of an installation and so on).



    Like a shark AJ ?


    It , the KMF, is not manufactured as an assembly to BS EN61439-3, as it is not a consumer unit.


    However, if there is only a KMF and no consumer unit- unlikely- then the intended use changes and would not be in the spirit of 421 etc.


    There are no steel moulded 800KMFs; though there briefly was, though to what BS is lost in time.


    Some may chose to manufacture a switch fuse to 61439-3, as opposed to the specific KMF.


    In the KMF, you cannot change the fuse holder. It is all in a moulded assembly. You could change the fuse, but that is not resetting a device as you would in a consumer unit. For most intended use the KMF is providing HRC fuse  protection usually upstream of a DBO  in a domestic. It is usually not touched by ordinary persons; they would be accessing the consumer unit. The KMF is just a bigger, beefier device than your 13 amp switch fuse connection unit and we do not usually require those to be steel.