How do you carry out testing (EFLI, PSSC, ect) on a 133/230Y system with a tester like this? It seems like every tester wants to see line neutral and earth. line, line, earth on the other hand triggers fault codes. 

https://www.fluke.com/en-us/product/electrical-testing/installation-testers/fluke-1662


Parents
  • I suspect you cannot do it in the way the makers intended, (looking at the manual ) as it is really intended for the 230/400v world. I'm a bit surprised to see it on sale in dollars - I;d have expected a US-centric tester to be very different.

    Do you have an N as well as an E ? 

    You may need to make in into a 2 wire tester and merge the role of N and E to measure phase to phase.

    There is no harm in calling Fluke and asking them.


    (contact info here )

    Are you actually in the USA or using American kit in 230V land ?

    M.
Reply
  • I suspect you cannot do it in the way the makers intended, (looking at the manual ) as it is really intended for the 230/400v world. I'm a bit surprised to see it on sale in dollars - I;d have expected a US-centric tester to be very different.

    Do you have an N as well as an E ? 

    You may need to make in into a 2 wire tester and merge the role of N and E to measure phase to phase.

    There is no harm in calling Fluke and asking them.


    (contact info here )

    Are you actually in the USA or using American kit in 230V land ?

    M.