Multi Function Testing

Former Community Member
Former Community Member
How do you carry out testing (EFLI, PSSC, ect) on a 133/230Y system with a tester like this? It seems like every tester wants to see line neutral and earth. line, line, earth on the other hand triggers fault codes. 

https://www.fluke.com/en-us/product/electrical-testing/installation-testers/fluke-1662


Parents
  • Can you do the lines to earth tests individually, L1 to earth then L2 to earth?




    Some Megger testers allow you alter what is being tested without actually moving the leads and test phase to phase.


Reply
  • Can you do the lines to earth tests individually, L1 to earth then L2 to earth?




    Some Megger testers allow you alter what is being tested without actually moving the leads and test phase to phase.