  • John Peckham:

    Out of interest are Zappi claiming compliance with BS EN 61008 for their electronic units in the Declaration of Conformity? I will be very surprised if an electronic device will meet all the requirements of BS EN 61008.


    If not you will need a separate BS EN 61008 Type A device upstream to comply with BS 7671 61008. 


    So it would appear not John. The declaration of conformity doesn’t mention 61008. How would it be permitted to claim compliance with a standard in the technical literature of a product when it is not? It matters not to me as there is always an upstream RCD installed but the Zappi is sold with the advantage of not needing a separate RCD. 

    what particular elements of 61008 do you think might be lacking?


Reply
  • John Peckham:

    Out of interest are Zappi claiming compliance with BS EN 61008 for their electronic units in the Declaration of Conformity? I will be very surprised if an electronic device will meet all the requirements of BS EN 61008.


    If not you will need a separate BS EN 61008 Type A device upstream to comply with BS 7671 61008. 


    So it would appear not John. The declaration of conformity doesn’t mention 61008. How would it be permitted to claim compliance with a standard in the technical literature of a product when it is not? It matters not to me as there is always an upstream RCD installed but the Zappi is sold with the advantage of not needing a separate RCD. 

    what particular elements of 61008 do you think might be lacking?