Minimum short circuit - Phase to Phase faults

Is it okay to consider only phase to phase faults for the end of line fault as it produces the minimum fault. Is there any probability of phase to earth or 3 phase faults getting lower than phase to phase faults.


Thank you!
Parents
  • There's certainly a possibility of L-PE faults having lower fault currents than a L-L fault - TT systems being the classic but even in TN systems a reduced c.p.c. or differing material for the c.p.c. (say steel armour rather than copper) will often result in higher impedance and hence lower currents for a L-PE fault. Also L-PE faults are normally driven by a lower voltage than L-L faults (say 230V rather than 400V) so will result in lower current even if the paths have the same impedance.

       - Andy,
Reply
  • There's certainly a possibility of L-PE faults having lower fault currents than a L-L fault - TT systems being the classic but even in TN systems a reduced c.p.c. or differing material for the c.p.c. (say steel armour rather than copper) will often result in higher impedance and hence lower currents for a L-PE fault. Also L-PE faults are normally driven by a lower voltage than L-L faults (say 230V rather than 400V) so will result in lower current even if the paths have the same impedance.

       - Andy,