Mixed IT and TN-S Earthing Systems

Hi, 

I'm installing Dd0yn11 transformers to supply 12-pulse VSDs; these require an IT system (I think). 

I will have other panels / motors etc. in the same area supplied from a Dyn11 (solidly earthed neutral) transformer i.e. TN-S system. 

Is there anything in BS7671 that tells me I can't have 2 earthing systems in the same area?

I would be grateful of any advice / guidance.

Thanks.
Parents
  • I guess "system earthing" (TN, TT etc) is explained (if not exactly defined in 312.2) (i.e. how the power system is earthed) while "earthing system" seems to be used consistently to mean the systems of conductors that connect exposed- and extraneous-conductive-parts to Earth. I agree some definitions would help to make it clearer though.


    Having two different systems with a common Earthing arrangement isn't uncommon - e.g. on construction sites we'd likely have a RLV transformer arranged as a TN-S system on its secondary, but it's means of Earthing will usually be the c.p.c. of the 230/400V primary circuit - which is likely part of a TT system. Ditto with some PELV systems.


      - Andy.
Reply
  • I guess "system earthing" (TN, TT etc) is explained (if not exactly defined in 312.2) (i.e. how the power system is earthed) while "earthing system" seems to be used consistently to mean the systems of conductors that connect exposed- and extraneous-conductive-parts to Earth. I agree some definitions would help to make it clearer though.


    Having two different systems with a common Earthing arrangement isn't uncommon - e.g. on construction sites we'd likely have a RLV transformer arranged as a TN-S system on its secondary, but it's means of Earthing will usually be the c.p.c. of the 230/400V primary circuit - which is likely part of a TT system. Ditto with some PELV systems.


      - Andy.