Hello All,
Could an unfused R.C.D. protected spur, from a complient ring final circuit, supplying a single outdoor socket via 1.5mm2 6242Y cable of max. length 300mm through a brick wall from an indoor socket outlet be considered compliant?
Z.
geoffsd:
I would maintain that the requirements of 433.1.204 for ring final circuits do not apply to the spurs but instead that the spurs are subject to the normal regulations - albeit you have not quoted anything which would prohibit what you have done.
Phew! Are you a politician Geoff? Well it was raining during the time of installation.
Z.
geoffsd:
I would maintain that the requirements of 433.1.204 for ring final circuits do not apply to the spurs but instead that the spurs are subject to the normal regulations - albeit you have not quoted anything which would prohibit what you have done.
Phew! Are you a politician Geoff? Well it was raining during the time of installation.
Z.