Unfused spur.

Hello All,


Could an unfused R.C.D. protected spur, from a complient ring final circuit, supplying a single outdoor socket via 1.5mm2 6242Y cable of max. length 300mm through a brick wall from an indoor socket outlet be considered compliant?


Z.
Parents
  • The regulations specifically allow 1.5 pyro for 32A rings, it is rated at 28A where contact is not possible, for clipped direct. It can get quite hot! 433.1.204, rating 20A minimum from installation method.
Reply
  • The regulations specifically allow 1.5 pyro for 32A rings, it is rated at 28A where contact is not possible, for clipped direct. It can get quite hot! 433.1.204, rating 20A minimum from installation method.