Unfused spur.

Hello All,


Could an unfused R.C.D. protected spur, from a complient ring final circuit, supplying a single outdoor socket via 1.5mm2 6242Y cable of max. length 300mm through a brick wall from an indoor socket outlet be considered compliant?


Z.
Parents


  • If it was a fused spur or indeed  1.5mm2 cable on an 13Aplug for an extension lead I'd have no issue, and unless you think someone will use one of those awful unfused 13A 2 way splits, a single socket is the same really.

     


    The single 13 Amp outside socket is going to be used for a car pressure washer I was told. I assumed that any load would be through a fused 13 Amp plug.


    Z.


Reply


  • If it was a fused spur or indeed  1.5mm2 cable on an 13Aplug for an extension lead I'd have no issue, and unless you think someone will use one of those awful unfused 13A 2 way splits, a single socket is the same really.

     


    The single 13 Amp outside socket is going to be used for a car pressure washer I was told. I assumed that any load would be through a fused 13 Amp plug.


    Z.