Hello All,
Could an unfused R.C.D. protected spur, from a complient ring final circuit, supplying a single outdoor socket via 1.5mm2 6242Y cable of max. length 300mm through a brick wall from an indoor socket outlet be considered compliant?
Z.
The IET is carrying out some important updates between 17-30 April and all of our websites will be view only. For more information, read this Announcement
AJJewsbury:
I'd check the 1.0mm² c.p.c. in the 1.5 T&E with the adiabatic carefully - it's probably not by the book on a B32 and the RCD is unlikely to help if the PFC is moderate to high.
- Andy.
Hi Andy, what range do you mean by moderate to high, thanks :)
AJJewsbury:
I'd check the 1.0mm² c.p.c. in the 1.5 T&E with the adiabatic carefully - it's probably not by the book on a B32 and the RCD is unlikely to help if the PFC is moderate to high.
- Andy.
Hi Andy, what range do you mean by moderate to high, thanks :)