Hello All,


Could an unfused R.C.D. protected spur, from a complient ring final circuit, supplying a single outdoor socket via 1.5mm2 6242Y cable of max. length 300mm through a brick wall from an indoor socket outlet be considered compliant?


Z.
Parents
  • If the RA is about 200 Ohms an L to E fault current is restricted in magnitude. And the 30 mA  R.C.D. is still very swift in disconnecting the fault. 


    Z.
Reply
  • If the RA is about 200 Ohms an L to E fault current is restricted in magnitude. And the 30 mA  R.C.D. is still very swift in disconnecting the fault. 