Unfused spur.

Hello All,


Could an unfused R.C.D. protected spur, from a complient ring final circuit, supplying a single outdoor socket via 1.5mm2 6242Y cable of max. length 300mm through a brick wall from an indoor socket outlet be considered compliant?


Z.
Parents
  • ebee:

    wasn`t the concern that someone did the sums for a BS3036 rewireable fuse using the 1.0 cpc and in some instances might be found wanting?


    And long before R.C.D.s were in use as well. So the earth fault could linger and cook the C.P.C. and insulation.


    Z.


Reply
  • ebee:

    wasn`t the concern that someone did the sums for a BS3036 rewireable fuse using the 1.0 cpc and in some instances might be found wanting?


    And long before R.C.D.s were in use as well. So the earth fault could linger and cook the C.P.C. and insulation.


    Z.