AJJewsbury:Zoomup:
If the Ra is about 200 Ohms an L to E fault current is restricted in magnitude. And the 30 mA R.C.D. is still very swift in disconnecting the fault.
Z.If the earth fault current is limited then I agree there's far less of an issue. Ra alone doesn't guarantee that though - bonding to metallic water or gas supplies can re-introduce a low impedance path (via neighbouring TN installations), so potentially bring prospective earth fault currents back up to TN levels.
- Andy.
Yes I suppose that the water pipe, if metal, could affect things. I did not check to see if it was plastic or metal. But I know that there is no mains gas as the owner said that he used bottled gas. He could not have a big under-lawn gas tank installed as the high water table would make it float and it could not be installed.
Z.
AJJewsbury:Zoomup:
If the Ra is about 200 Ohms an L to E fault current is restricted in magnitude. And the 30 mA R.C.D. is still very swift in disconnecting the fault.
Z.If the earth fault current is limited then I agree there's far less of an issue. Ra alone doesn't guarantee that though - bonding to metallic water or gas supplies can re-introduce a low impedance path (via neighbouring TN installations), so potentially bring prospective earth fault currents back up to TN levels.
- Andy.
Yes I suppose that the water pipe, if metal, could affect things. I did not check to see if it was plastic or metal. But I know that there is no mains gas as the owner said that he used bottled gas. He could not have a big under-lawn gas tank installed as the high water table would make it float and it could not be installed.
Z.