Unfused spur.

Hello All,


Could an unfused R.C.D. protected spur, from a complient ring final circuit, supplying a single outdoor socket via 1.5mm2 6242Y cable of max. length 300mm through a brick wall from an indoor socket outlet be considered compliant?


Z.
Parents
  •  but as this is an unfused spur that doesn't really help for faults before the socket.

       - Andy.


    The 1.5mm2 6242Y is no longer than 300mm and runs through a brick wall. It starts from a deeply sunk double metal box and terminates at a surface mounted all insulated 13 Amp. I.P. 64 rated single 13 Amp socket. Any physical damage is very unlikely.


    Z.