Hello All,
Could an unfused R.C.D. protected spur, from a complient ring final circuit, supplying a single outdoor socket via 1.5mm2 6242Y cable of max. length 300mm through a brick wall from an indoor socket outlet be considered compliant?
Z.
The 1.5mm2 6242Y is no longer than 300mm and runs through a brick wall. It starts from a deeply sunk double metal box and terminates at a surface mounted all insulated 13 Amp. I.P. 64 rated single 13 Amp socket. Any physical damage is very unlikely.
The energy let through you are quoting is at the DB with 6kA PSCC (or 3kA) .... The other points to consider are the PSCC at the point the 1.0 Earth conductor joins, which will not be 6kA or even 3kA, it might be as high as 575A if the ring is short and the DB PSSC high. The by the book calculation is not a theoretical possible maximum value, it is an actual value.
The 1.5mm2 6242Y is no longer than 300mm and runs through a brick wall. It starts from a deeply sunk double metal box and terminates at a surface mounted all insulated 13 Amp. I.P. 64 rated single 13 Amp socket. Any physical damage is very unlikely.
The energy let through you are quoting is at the DB with 6kA PSCC (or 3kA) .... The other points to consider are the PSCC at the point the 1.0 Earth conductor joins, which will not be 6kA or even 3kA, it might be as high as 575A if the ring is short and the DB PSSC high. The by the book calculation is not a theoretical possible maximum value, it is an actual value.