AJJewsbury:So, if the two items mentioned are not exposed-conductive-parts they need no bonding.
That may be true of the general principle of supplementary bonding (415.2) but in bathrooms the requirement is extended to include the c.p.c. supplying Class II (double insulated) equipment (701.415.2) - no doubt to guard against DIYs replacing fittings with class I ones (in alignment with 412.2.3.2).
Presuming supplementary bonding is required of course.
- Andy.
-
And we must not forget that a flex C.P.C. can be used as a supplementary bonding conductor for a fixed appliance, say to a heated towel rail or wall heater.
544.2.5
Z.
AJJewsbury:So, if the two items mentioned are not exposed-conductive-parts they need no bonding.
That may be true of the general principle of supplementary bonding (415.2) but in bathrooms the requirement is extended to include the c.p.c. supplying Class II (double insulated) equipment (701.415.2) - no doubt to guard against DIYs replacing fittings with class I ones (in alignment with 412.2.3.2).
Presuming supplementary bonding is required of course.
- Andy.
-
And we must not forget that a flex C.P.C. can be used as a supplementary bonding conductor for a fixed appliance, say to a heated towel rail or wall heater.
544.2.5
Z.