Kris H:
I get it.
I just thought the idea of a forum was to see what your peers thought. No different to working in an office an putting opinions across - but I am on my own now so sometimes looking for a 2nd opinion.
Cheers
Quite right Kris,
the forum should be here to help others. You were brave and right to ask Kris. I hope that you have not been put off from asking again in the future.
Good luck,
Z.
So, if the two items mentioned are not exposed-conductive-parts they need no bonding.
AJJewsbury:So, if the two items mentioned are not exposed-conductive-parts they need no bonding.
That may be true of the general principle of supplementary bonding (415.2) but in bathrooms the requirement is extended to include the c.p.c. supplying Class II (double insulated) equipment (701.415.2) - no doubt to guard against DIYs replacing fittings with class I ones (in alignment with 412.2.3.2).
Presuming supplementary bonding is required of course.
- Andy.
-
And we must not forget that a flex C.P.C. can be used as a supplementary bonding conductor for a fixed appliance, say to a heated towel rail or wall heater.
544.2.5
Z.