mapj1:
We need the OP to come back and clarify - I had read it that there were exposed parts, as part of whatever the process is, and the question is more is unplugging and visual verification better than a switch.
If not a pilot light would be a better design
My understanding was that the supply is isolated and locked off. Then a lid is removed and before any further work is undertaken, the supply is proved dead.
The alternative which has been proposed is to isolate by removing the plug so that proving dead is unnecessary. IMHO, that is fine provided that the plug remains under the control of the technician in the same way as the key of the padlock would be.
mapj1:
We need the OP to come back and clarify - I had read it that there were exposed parts, as part of whatever the process is, and the question is more is unplugging and visual verification better than a switch.
If not a pilot light would be a better design
My understanding was that the supply is isolated and locked off. Then a lid is removed and before any further work is undertaken, the supply is proved dead.
The alternative which has been proposed is to isolate by removing the plug so that proving dead is unnecessary. IMHO, that is fine provided that the plug remains under the control of the technician in the same way as the key of the padlock would be.