Sparkingchip:
528.3.3 requires a common main protective bonding conductor to be continuous, so that is a pipe clamp or the like is removed the conductor remains as a single length of cable.
I think that has been taken out of context. 528.3 is all about protecting the wiring from water, heat, fumes; plumbers, and gas fitters.
Bonding is not in proximity to other services; it is in contact with them.
Where both main gas pipes and main water pipes enter a location, a common bonding conductor may be used, but in such cases that conductor should be continuous or should be permanently jointed (by soldering or crimping) in order to preserve continuity.

davezawadi (David Stone):
The NAPIT man is simply wrong (and therefore should be prevented from carrying out any certification or EICR work)
Regards
David
That's a bit harsh, he may have got over 99% of the questions in the Wiring Regulations exam correct. ?