Radial Voltage Drop Calculation?... By Load or MCB Rating?

I'm doing the calculation for total voltage drop.  I have 14 radials/ways going out.  As I understand it, that would equal a max allowance of 0.285% voltage drop per radial/way.  Or some sort of mixture throughout not exceeding the 4% drop allowance overall.  Firstly, is this correct? 


Secondly, should I be doing my calculations based on actual Load or the MCB ratings of the individual radials/ways? 


Thanks in advance!
Parents
  • Thanks all.  Oh right!?... I was of the understanding that the allowance is for the whole installation?...

    https://www.tlc-direct.co.uk/Book/4.3.11.htm
    Qoute form Example 4.8 from the above link:-  "It is important to appreciate that the allowable volt drop of 4% of the supply voltage applies to the whole of an installation. If an installation has mains, sub-mains and final circuits, for instance, the volt drop in each must be calculated and added to give the total volt drop as indicated in {Fig 4.10}."


    ...is that incorrect?  Cheers!
Reply
  • Thanks all.  Oh right!?... I was of the understanding that the allowance is for the whole installation?...

    https://www.tlc-direct.co.uk/Book/4.3.11.htm
    Qoute form Example 4.8 from the above link:-  "It is important to appreciate that the allowable volt drop of 4% of the supply voltage applies to the whole of an installation. If an installation has mains, sub-mains and final circuits, for instance, the volt drop in each must be calculated and added to give the total volt drop as indicated in {Fig 4.10}."


    ...is that incorrect?  Cheers!