Radial Voltage Drop Calculation?... By Load or MCB Rating?

I'm doing the calculation for total voltage drop.  I have 14 radials/ways going out.  As I understand it, that would equal a max allowance of 0.285% voltage drop per radial/way.  Or some sort of mixture throughout not exceeding the 4% drop allowance overall.  Firstly, is this correct? 


Secondly, should I be doing my calculations based on actual Load or the MCB ratings of the individual radials/ways? 


Thanks in advance!
Parents
  • Also, Broadgage, LED lighting is not ohmic in response, so this too should not be a problem They are not a few LEDs in series with a resistor, even a simple light bulb has a full-on feedback stabilized switch mode power supply, so all bulbs at any reasonable voltage should be the same brightness. Dimmable ones are a bit different they modify the feedback by the mains peak voltage, to make them dim at all!
Reply
  • Also, Broadgage, LED lighting is not ohmic in response, so this too should not be a problem They are not a few LEDs in series with a resistor, even a simple light bulb has a full-on feedback stabilized switch mode power supply, so all bulbs at any reasonable voltage should be the same brightness. Dimmable ones are a bit different they modify the feedback by the mains peak voltage, to make them dim at all!