Radial Voltage Drop Calculation?... By Load or MCB Rating?

I'm doing the calculation for total voltage drop.  I have 14 radials/ways going out.  As I understand it, that would equal a max allowance of 0.285% voltage drop per radial/way.  Or some sort of mixture throughout not exceeding the 4% drop allowance overall.  Firstly, is this correct? 


Secondly, should I be doing my calculations based on actual Load or the MCB ratings of the individual radials/ways? 


Thanks in advance!
Parents
  • Run around on tray.

    How are you attaching the cables to the tray? Bear in mind that supporting cables only using plastic devices (e.g. nylon cable ties) is no longer permitted.




    Cheers Andy.  Cables will be on top of horizontal tray, I understand that plastic cable ties are fine for attaching in this situation?  Is that correct?  Any vertical or horizontal cable runs without tray support will be clipped direct using metal wall cable clips.

    Re Cable choice - what options would you personally go for?

    Main cable runs to power sockets and/or isolators around perimeter on tray and clipped direct, all above 1m from ground - NYY?  SWA?

    Secondary cable runs from Isolator (1m above ground) to Element (30cm above ground) -  CY?  NYY?  SWA?


    Cheers!


Reply
  • Run around on tray.

    How are you attaching the cables to the tray? Bear in mind that supporting cables only using plastic devices (e.g. nylon cable ties) is no longer permitted.




    Cheers Andy.  Cables will be on top of horizontal tray, I understand that plastic cable ties are fine for attaching in this situation?  Is that correct?  Any vertical or horizontal cable runs without tray support will be clipped direct using metal wall cable clips.

    Re Cable choice - what options would you personally go for?

    Main cable runs to power sockets and/or isolators around perimeter on tray and clipped direct, all above 1m from ground - NYY?  SWA?

    Secondary cable runs from Isolator (1m above ground) to Element (30cm above ground) -  CY?  NYY?  SWA?


    Cheers!