This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

Reducing cable sizes for termination agasint volt drop

Hopefully a straight forward question:- I have a development where the submains supply is 70mm² XLPE/SWA/LSF  and this is largely down to the length of run (volt drop) opposed to the current carrying capacity. However at the source end of the cable the meter that’s been installed cannot accommodate this size of cable so installing this through an isolator first can the cable size then be reduced to fit in the meter. The small cable would still be well with the current carry capacity of the circuit and line with the protection device? What are peoples thoughts? Bad practice??



Parents
  • Thanks right it's a private meter.
Reply
  • Thanks right it's a private meter.
Children
No Data