TurkishBreakfast:
Hi,
I am preparing the kitchen in my flat for a rewire and need to run cables for 2 x ovens plus dishwasher, washing machine, fridge freezer etc.
The flat has solid ceilings and floors and CU is on opposite side of the flat from the kitchen so running cable is a challenge. When we rewire the rest of the electrics, the sockets and lights are likely to go either behind coving or chased into plaster, but this is not really feasible for the kitchen cables.
Digging trenches in concrete floors may weaken them. Professional advice is recommended from a structural engineer. Why not run your cables behind the kitchen base units at floor level?
Z.
TurkishBreakfast:
I’m thinking my best option is to go through the floors.
I do hope that this flat is on the ground floor. (ETA: answer provided whilst I was typing.)
Not really a wiring question!
As Mike says, make sure that the sub-floor is not structural if you go into it. I would add that you do not want to breach any damp-proof membrane.
Back to BS 7671 ...
Section 522 - external influences - is relevant. You need to avoid or protect against water (522.3), corrosive substances (522.5), impact (522.6) and any other intended use (522.8.7). It might be possible to achieve that with a shallow chase, possibly covered by no more than floorboards (natural or engineered).
If you want to use conduit, it must be installed before the cables are drawn in (522.8.2).
Whatever option you choose, it would be wise to discuss with your chosen electrician beforehand. It might be a bit upsetting if somebody came later on and declined to accept what had been done.
Sparkymark:
Just a thought, have you got space in the kitchen where you could put a small consumer unit?
Then you could just run one suitably sized swa to the kitchen and new circuits could be connected to the new consumer unit.
I was thinking exactly the same whilst reading down the thread. Terminating several SWA cables might be problematic with some domestic CU's. A second C.U makes it easier for future additions as well.
Gary
davezawadi (David Stone):
Advice for any more grooving of floors and walls. Hire a chasing machine for a day and a suitable vacuum cleaner. It then makes little mess, and virtually no dust in the air. So much better. I have a Makita one, really excellent with my Henry! A few mm into the floor will make no difference to the strength, this part is in compression and well strong enough. It is the underside, in tension, which could be damaged, avoid the reinforcement, which will be near the underside! 20mm steel conduit will do the job, whilst plastic will work, I always prefer steel buried in concrete. 10mm of strongish mortar over the top will finish the job. You say 4 bends, this is OK if you only have a small number of cables (small fill factor). Cable current rating installation method B from table 4D1A. Overall this is much easier than SWA, and tidier too, because SWA doesn't sit nicely in place whilst you fill in and is probably bigger in diameter!
We used to limit 90 degree bends to 2 no. max in any one single run between access points. Has this been relaxed? Also the regs. require the conduit system to be fully installed between access points before cables are pulled in. 522.8.2
Has anyone considered the expansion and contraction of metal or plastic conduit due to temperature changes. This may disturb shallow screeding.
Z.