This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

An interesting issue with a TT supply

An interesting real life example of why you need double pole switching with a TT supply. The scenario is a small village with a few customers supplied by a single pole mounted transformer. 


We got a call from an electrician working in a property who had measured 400V phase to earth, 210V neutral to earth, and 241V phase to neutral, and was understandably worried. Any suggestions of what I tracked the fault down as? This can happen on any TT supply, but is fortunately very rare - I have come across it three times in 20 years. 


Regards,


Alan.
Parents
  • My guess.

    shared but isolated water service.

    Neighbours faulty or non existant rcd. Neighbour on second phase with fault to earth.
Reply
  • My guess.

    shared but isolated water service.

    Neighbours faulty or non existant rcd. Neighbour on second phase with fault to earth.
Children
No Data