An interesting issue with a TT supply

An interesting real life example of why you need double pole switching with a TT supply. The scenario is a small village with a few customers supplied by a single pole mounted transformer. 


We got a call from an electrician working in a property who had measured 400V phase to earth, 210V neutral to earth, and 241V phase to neutral, and was understandably worried. Any suggestions of what I tracked the fault down as? This can happen on any TT supply, but is fortunately very rare - I have come across it three times in 20 years. 


Regards,


Alan.
Parents
  • There are plenty of three phase PMTs around.  Smaller PMTs tend to be single or split phase.  Generally up to 100kVA on a single pole and up to 200kVA on either an H pole or pole with a stub pole, Tf sits on steelwork between the two..  I have seen bigger than 200kVA but not very often.  IIRC pole mounted substations are exempt from business rates which I think are charged on ground mounted.
Reply
  • There are plenty of three phase PMTs around.  Smaller PMTs tend to be single or split phase.  Generally up to 100kVA on a single pole and up to 200kVA on either an H pole or pole with a stub pole, Tf sits on steelwork between the two..  I have seen bigger than 200kVA but not very often.  IIRC pole mounted substations are exempt from business rates which I think are charged on ground mounted.