An interesting issue with a TT supply

An interesting real life example of why you need double pole switching with a TT supply. The scenario is a small village with a few customers supplied by a single pole mounted transformer. 


We got a call from an electrician working in a property who had measured 400V phase to earth, 210V neutral to earth, and 241V phase to neutral, and was understandably worried. Any suggestions of what I tracked the fault down as? This can happen on any TT supply, but is fortunately very rare - I have come across it three times in 20 years. 


Regards,


Alan.
Parents
  • A few have the answer, with Geoff Blackwell spotting it first. The electrician was doing other work in the property, and found the problem while proving dead. 


    One of the other properties in the village had a single phase submain with an earth fault, and a non—operative main rcd feeding it.


    We used the famous “screwdriver in the flowerbed” to identify which phase had gone wrong, then tried a few properties our records said were on that phase, before settling on a riding stables with a three phase supply. As only one phase was affected by the fault, we removed one fuse from their cutout and asked them to call an electrician to locate their fault. The fault was located, and we drew our remaining fuses to allow the electrician to replace the customer’s main rcd, then replaced and re-sealed all three fuses. 


    Regards,


    Alan.
Reply
  • A few have the answer, with Geoff Blackwell spotting it first. The electrician was doing other work in the property, and found the problem while proving dead. 


    One of the other properties in the village had a single phase submain with an earth fault, and a non—operative main rcd feeding it.


    We used the famous “screwdriver in the flowerbed” to identify which phase had gone wrong, then tried a few properties our records said were on that phase, before settling on a riding stables with a three phase supply. As only one phase was affected by the fault, we removed one fuse from their cutout and asked them to call an electrician to locate their fault. The fault was located, and we drew our remaining fuses to allow the electrician to replace the customer’s main rcd, then replaced and re-sealed all three fuses. 


    Regards,


    Alan.