Weirdbeard:Hi Wally, wouldn’t those types of equipment need local surge protection to protect them? I was under the impression that a surge protector covering the whole installation protects only the installation itself, such as electronic RCBOs etc.
The point of a type 2 SPD at the origin or DB is to reduce a 4kV transient in the installation down to a 1.5kV spike. The individual bits of electronic equipment like LEDs are then supposed to be able to cope with a 1.5kV spike - or if not, then a type 3 SPD should be installed next to them.
Weirdbeard:Hi Wally, wouldn’t those types of equipment need local surge protection to protect them? I was under the impression that a surge protector covering the whole installation protects only the installation itself, such as electronic RCBOs etc.
The point of a type 2 SPD at the origin or DB is to reduce a 4kV transient in the installation down to a 1.5kV spike. The individual bits of electronic equipment like LEDs are then supposed to be able to cope with a 1.5kV spike - or if not, then a type 3 SPD should be installed next to them.